UPS or not UPS, that is the question
I just found that my UPS eats about 140W in addition to my servers.
It is online UPS 9130i 1000R
Servers eats 380W but all together it is 520W.
I didnt measured yet how much my offline UPSs eats, but i hope it is much less than that.
so this big amount of cost makes me question is it worth to use UPS?
How often do you have power outage ? In terms of hours per week or month.
in last half a year had 2 of them, with 1h and 2h so UPS do not help
Then in my opinion, it is not worth adding UPS to the mix. Use those 1h and 2h for maintenance instead like cleaning around the servers or inside the servers.
Online UPSes are the least efficient since they are always converting from AC to DC then back to AC. An offline or line-interactive UPS will have significantly lower waste.
Usually the power outages happen at the most inconvenient time and to clean the servers I need my air compressor which needs electricity.
My big UPS converts more power into heat, because it is a more powerful model and somewhat old. I also have a generator.
An on-line UPS is less efficient, but it can clean up the power, output a different voltage from input and run from somewhat degraded input (voltage out of spec for example). In my case, the generator produces power that not all devices (particularly off-line UPSs) like, but the big UPS can clean it up.
I can totally relate to that but I use a simple painting brush and blow air with my mouth or just use a big cardboard and blow some air on it. The hour just goes by doing all that.
If this is the Eaton UPS you should try “High Efficiency mode”, which basically makes it an Offline UPS.
I have a couple of APC UPS and they’ve been quite handy in gracefully shutting off my servers when there is an outage for more than a minute.
ok thanks for info, I didnt know that something like this is possible.
In addition for switching to standby UPS, if you don’t have brownouts and fairly stable power where when shuts off it’s shuts off cleanly and infrequently — you can consider disabling write caching, re-enabling sync, and removing UPS. With current low load it shall be feasible.
Holy … cow… I have been completely oblivious to this distinction previously.
Great, something to add to my To-Do list.
Thanks…
… and I mean that.
2 cents,
Julio